12387Why is it so important to suck back as much freon liquid as possible from the evaporators, before You stop the compressor?
to prevent environment you shouldn't let refrigerant go to atmosphere. Must suck all before compressor change.
0
Reply
elreedy   18-Feb-2016 16:41
Because if you stop the compressor direct without keep it in low pressure stop the freon will keep high and it may increase due to any liquid back in the return line also and after a while it will convert to vapor which will lead to increase the pressure in suction line and when you try to start the compressor the pressure will be high on the piston and will lead to increase the consumed ampere and it may trip as well.
0
Reply
pravinghadgesis   16-Mar-2019 10:24
There are Couple of reasons for sucking/ collecting the ref gas in condenser before stopping the ref. compressor they are as follows
1. as the environment temp increases the ref pressure will increase any ref gas /liquid in the system will expand which can cause a rupture / unwanted leakages in the system.
2. AS correctly said in the above for maintenance purposes.
0
Reply
pakasi   17-Jan-2021 06:31
maybe you mean pump down? pump down is important when you decide to not use your system for a long time.
when compressor stop for long time the refrigerant inside the evaporator might become liquid form and it's bad for your compressor to suck a liquid at large volume rather than gas, another reason is oil from compressor isn't 100% separated in oil separator. therefore there is oil inside your evaporator. when you stopped your compressor for a long time the oil and the liquid refrigerant will mixed together and return into comp crankcase when you run your system which isn't good for your comp lubrication. there is more reasons to pumping down your system.
0
Reply
shcherbakov   20-Jan-2021 15:35
74107not use your system for a long time
any time. operator of ref plant must read instruction manual. if ref plant compressor stopped by operator - usually way collect all freon in liquid receiver and condenser. it is safety matter for equipment and crew.
0
Reply
   Attach screenshots
Heads necessary to send messages to enable JavaScript
refresh list

Similar topics

The Personal Cybersecurity Manual - Marlon Buchanan [2022, M4B]
Boiler Water Treatment - J. D. SKELLY, B.Sc., Chart. Chemist, M.R.I.C. [1990, PDF]
The Sea Was Angry - Armand Rosamilia [2020]
Bernard Moitessier Joshua Steel Sailboat Yacht Boat Plan - Moitessier B. [2017, JPEG]
Joshua Steel Yacht Plan - Moitessier B. [1968, JPEG]
LPG TANKER (VLGC) CARGO GAS COMPRESSOR MANUAL
Instruction Book for Atlas Copco Deck Air Compressor (GA11, GA15, GA18, GA22, GA30C) - Atlas Copco…
Operation Instruction BA COMPRESSOR LW 100 Series - LW [2013, PDF]
Yanmar SC10N SC7N SC12,5N Parts Catalog - Elrohir [2018, PDF]
The Importance of Cargo Sampling - Japan P&I [2019, PDF]
LOAD MORE
  • Reply

The time now is: Today 20:30

All times are GMT + 3 Hours